[GBlist]Outdoor combustion air supplies
At 08:15 AM 2001-02-22 -0700, mac12 wrote:
>A note of caution:
>
>As we work harder to seal buildings for energy efficiency (or perhaps to
>reduce radon infiltration), we run the risk of not having a source for
>combustion air. Picture a perfectly sealed basement with a furnace using
>room air for combustion. You would have a bad case of negative pressure
>in the basement which would prevent combustion products from exhausting up
>the flue. (snip)
This is a complicated issue. Excessive negative pressure in the basement is
actually more likely to result from pot lights in a cathedral ceiling than
from air consumption by a furnace.
We did a study a number of years ago on masonry heaters, and concluded that
if the air consumption was under 30 litres/sec (64 cfm), there was no
chance of the appliance causing appreciable depressurization, even in the
tightest house that we could find, which had an Equivalent Leakage Area of
25 sq. in.
There is a good discussion of outdoor combustion air supplies by John
Gulland at
http://www.woodheat.org/outdoorair/outdoorair.htm
Best ........ Norbert Senf
----------------------------------------