>...whether or not to vent the cathedral ceiling/roof ...that will
>be insulated with dense-packed cellulose.
Whitney & Tristan;
Theoretically, you should not need to vent the ceiling/roof if the interior air
barrier at the ceiling is perfectly air-tight.
In reality, $#!+ happens and theory (as well as the air barrier) is, more often
than not, imperfect.
In addition to the likelihood of an imperfect air barrier, the reality of "$#!+
happens" also means that moisture will likely find other ways to get where it's
not intended to go.
Without a ventilation airspace to permit moisture to cook off in the event that
it does find its way into the ceiling insulation, damage is almost certain to
occur.
In providing a ventilation airspace to accommodate drying, you lose a bit of
space that otherwise could have gone towards insulation. That lost R-value is
pretty easy to regain elsewhere.
--- * ---
Rob Tom
Kanata, Ontario, Canada
(remove the "chaff" from my edress if you hit "reply")
Please visit http://www.theHungerSite.com daily
______________________________________________________________________
This greenbuilding dialogue is sponsored by REPP/CREST, creator of
Solstice http://www.crest.org, and BuildingGreen, Inc., publisher of
Environmental Building News and GreenSpec http://www.BuildingGreen.com
______________________________________________________________________
 |
 |
|